8/15/2013 5:33 PM | |
Joined: 4/22/2010 Last visit: 10/17/2024 Posts: 5697 Rating: (715) |
Hello, You need to update OS with the option reset to factory defaults by using Prosave, this to avoid the settings in control panel. How do you do an operating system update (OS update) on operator panels? Read the ProSave pdf, chapter 1.2 might save your job Regards, Marcjan |
Last edited by: Marcjan at: 8/15/2013 5:35 PMProblem solved? |
|
8/16/2013 10:19 AM | |
Posts: 3037 Rating: (192)
|
Hello, You do not know the password of control panel, then you can only do an OSUpdate with reset to factory settings. http://support.automation.siemens.com/WW/view/en/23800567 http://support.automation.siemens.com/WW/view/en/23802404 http://support.automation.siemens.com/WW/view/en/19142034 Tweety |
8/20/2013 8:44 AM | |
Joined: 4/22/2010 Last visit: 10/17/2024 Posts: 5697 Rating: (715) |
Hello, I have not restored this panel, but several others with succes. The trick that prosave does is catching the panel boot loader before it can start the OS. That's why you have to shut it down and startup after starting the OS update. What version of prosave you have there? I have 9.0 and can select Ethernet. See picture. You can download the latest version (10) Servicetool SIMATIC ProSave Regards, Marcjan |
Problem solved? |
|