1/16/2020 3:02 AM | |
Joined: 12/27/2018 Last visit: 10/2/2024 Posts: 510 Rating: (43) |
A similar thread in this link. |
Jinson James, M.Tech (Power Electronics and Power System), |
|
1/16/2020 9:46 AM | |
Joined: 8/3/2009 Last visit: 10/31/2024 Posts: 14079 Rating: (1765)
|
Hello Do you have a Basic Panel or a Comfort Panel (they are called both KTP400). In Comfort Panel you can set a Time Zone in Basic PAnels you can set a Time Shift -> If you want to synchronize the PLC and the HMI then look at this: https://support.industry.siemens.com/cs/ww/en/view/69864408 https://support.industry.siemens.com/cs/de/en/view/109482675 Bye Murof |
If this Information really helps, you could use the Rate function |
|