Hi, if you use a CP342-5 you will need functions DP_SEND/DP_RECV for communication. Please check this FAQ: What should you watch out for when configuring a CP342-5 as DP master and why is it necessary to call the FC1 "DP_SEND" and FC2 "DP_RECV" functions in the user program of the CPU in order to transfer data?Regards, Towome |
|
|
This contribution was helpful to1 thankful Users |
12/9/2021 8:41 AM | |
Joined: 4/24/2006 Last visit: 11/19/2024 Posts: 8770 Rating: (1171)
|
Hello, The CP342-5 is a DPV0 master and the IM155-6 needs a DPV1 master. So I guess that is the problem. How can you tell whether your S7-300/400 master supports DPV1 functions? You need another master to use this slave. Best regards, Wizard |