4/11/2016 7:36 PM | |
Posts: 45 Rating:
|
This is for my m2m |
Last edited by: NACHATE at: 4/13/2016 9:42:24 AM |
|
4/11/2016 10:13 PM | |
Joined: 8/31/2013 Last visit: 5/26/2024 Posts: 607 Rating:
|
Hello Please find the attached File Only You have to call FC76 it explains its self AttachmentAbb_prof.zip (79 Downloads) |
Warm Regards |
|
This contribution was helpful to
1 thankful Users |
4/11/2016 10:18 PM | |
Joined: 9/27/2006 Last visit: 7/13/2024 Posts: 12268 Rating:
|
Hello Nachate; So now you have the gsd files you required earlier. The nest steps you could easily have found yourself, using Google or Siemens Support (in the case of the Siprotec relay)...
Data exchanged over Profibus-DP with a Siprotec relay is organized in telegrams called "mappings" that you cannot change, so study the different mappings available for your relay and choose the one that gives you the required data with the minimum amount of registers transfered. In your configuration you have chosen modules that give you 64 words IN (of which 16 are consistent data, not good: all should be consistent, or none); for your application build the number of words read in and out to match your selected mapping size. You also must configure the relay through DIGSI in order to enable comms over the relay's Profibus-DP interface (in the back of the relay), select the Profibus address of the relay, choose the selected mapping and the settings for the relay's Input/Output digital signals. through and enable these settings in the relay's programming before you can exchange data over Profibus-DP.
PowerFlex 20-COMM-P Profibus Adapter User Manual Application Note PowerFlexDC & 20-COMM-P Adapter with Siemens s7-315-2DP
https://library.e.abb.com/public/21798dec4bb52463c1257b160061f755/M2M%20PROFIBUS_2CSG445013D0201.pdf The DP-master in this case is an ABB AC500, but you can easily apply the same type of module selection and programming in the S7 PLCs. Now, there is a point where you have to do the development yourself. You now have the gsd files and the communication manuals for these Profibus slaves. You must take time to study the provided documents, choose the right configurations and implement them in your PLC program. This is the way we have to do our own programs. That is the only way you will learn. Hope this helps, Daniel Chartier
|
Last edited by: dchartier at: 4/16/2016 7:37:04 PM |
|
This contribution was helpful to
1 thankful Users |
4/12/2016 11:53 AM | |
Posts: 45 Rating:
|
Thank you beautiful People for your answer, I have to use as the attachment the 'SFC 14 and SFC 15" to read and write ?? |
4/12/2016 12:34 PM | |
Joined: 8/31/2013 Last visit: 5/26/2024 Posts: 607 Rating:
|
Hello Again Yes you have to use them |
Warm Regards |
|
4/16/2016 7:08 PM | |
Posts: 45 Rating:
|
Hello, I did this is it good ? (Forgive me I'm new in this domain and I prepare my final exam) |