Hello all Thank you for the this guide really helpful. I encountered this issue also when try communication with my flow meter. I am using the Modbus ET200S card 6ES7138-4DF11-0AB0 What I did to solve the issue is that. a) Change A / B cable. My work setting now is Modbus card(A) to (Flowmeter)B and Modbus card(B) to Flowmeter(A) b) I also change my function code in my program to FC03 Even though in manual mentioned FC03 - Read Output Register, But this I think also depend on the flowmeter. In my flowmeter manual got mentioned need to use FC03 to access the register Hope some info helps Regards, Faizal
------------------------------------------------------------------------------------------ |