4/10/2013 4:44 PM | |
Joined: 11/8/2011 Last visit: 8/21/2024 Posts: 387 Rating: (43) |
hi naofel please have look here discussion and FAQ |
4/10/2013 4:54 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715) |
Hello, A complete list with Step7 error codes you will find here: What is the meaning of the error codes (xxxx:yyyy) in STEP 7? 33:16662 Online: No connection. Node does not accept the connection setup. The partner is neither a CPU nor a CP. Check that the configuration and the actual hardware configuration match. |
Last edited by: Marcjan at: 4/10/2013 4:55 PMProblem solved? |
|
4/15/2013 12:38 PM | |
Posts: 11 Rating: (0) |
Thank u for your help. I resolved the problem. But another question please : If i make the switcher in MRES position, the program will be lost or no? |
4/15/2013 8:05 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715) |
Hello, If you set it to Mres, the program will not be lost. To clear the PLC you have to follow a procedure explained here: How do you reset a SIMATIC S7-300 CPU and MMC (default reset or overall reset)? Regards, Marcjan |
Problem solved? |
|
This contribution was helpful to1 thankful Users |
4/22/2013 1:02 PM | |
Posts: 11 Rating: (0) |
Thanks. |
9/18/2013 1:59 PM | |
Joined: 4/24/2009 Last visit: 8/20/2024 Posts: 2682 Rating: (135) |
New question was splitted to how to go online with 300? Best regards O_Moderator |