4/23/2013 2:22 PM | |
Posts: 1547 Rating: (129)
|
Hello, to use the CP342-5 as DP Slave you have to use a GSD File on OMRON side. The GSD file you will find here: PROFIBUS GSD files : SIMATIC Check on OMRON side the PROFIBUS address you have configured there, because if the address is right then it will work or you will get another error message like Station found, but wrong configuration. Check also cabling or use CP special diagnostic to check live list if PROFIBUS Address of OMRON Station will be found. |
This contribution was helpful to1 thankful Users |
4/25/2013 12:28 PM | |
Posts: 9 Rating: (0) |
Here I have que diagnostic of the cp342-5 slave.
Attachmentdiagn.pdf (182 Downloads) |
Last edited by: ArielP at: 4/25/2013 12:40 PM |
|
4/25/2013 12:40 PM | |
Joined: 9/27/2006 Last visit: 9/13/2024 Posts: 12282 Rating: (2683) |
Hello Ariel; You seem to have had difficulty in uploading your diagnostic information. Please try again. Two questions: First, did you insert FC1 and FC2 in your Step 7 rpogram, to support the CP 342-5? If this is already done, it would be good to see how they have been configured. Second: what adrress range have you configured in the CP 342-5 compared to FC1 and FC2?Have a look at the following FAQ and attached links: Notes on linking a CP342-5 as DP slave to a DP master with STEP 7 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 4/25/2013 12:41 PM |
|
4/25/2013 3:03 PM | |
Joined: 9/27/2006 Last visit: 9/13/2024 Posts: 12282 Rating: (2683) |
Hello Ariel; In your diagnostic messages a few stand out, at first glance
Translation from the Spanish:
The statements from the diagnostic buffer show that your configuration is inconsistent. Your first step should be to checkthe Profibus configuration of the slave, comile the HWConfig to regenerate the SDBs and download the configuration to the CPU once more. If the BF LED starts up only when you connect to the Profibus master,, I would check also how FC1 and FC2 have been confoigured. please open the links in the proposed FAQ above, and also the information on FC!/FC2 here: What should you watch out for when configuring a CP342-5 as DP master and why is it necessary to call the FC1 "DP_SEND" and FC2 "DP_RECV" functions in the user program of the CPU in order to transfer data? Hope this helps, Daniel Chartier |
1/12/2017 12:35 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
New question published by JoseLuisMoreno is split to a separate thread with the subject GSD file of OMRON C1JW-PRM21 Profibus Master. Best regards |