Joined: 12/1/2009 Last visit: 10/27/2024 Posts: 672 Rating: (147) |
Hi NICHOL, this is very long time back and I don't even rememberin detail. This is what I got from the document (link below). "The S5-95U can function on the SINEC L2-DP bus as slave node only." http://cache.automation.siemens.com/dnl/jU/jU2OTA1AAAA_1091098_HB/6ES5%20998-8MD21.pdf Good Luck! |
Last edited by: TIBI68 at: 8/11/2014 5:59 PMGive us your feedback and show us your respect! |
|
8/12/2014 4:38 AM | |
Joined: 10/7/2005 Last visit: 11/13/2024 Posts: 3027 Rating: (1057)
|
Hello NICHOL
You must and can only download it to the 32Kbyte EEPROM which is mandatory to have if you use the 095-8MExx as a DP Master(12Kbyte of the EEPROM is reserved for the DP master config file). Note that a small entry in DB1 is also required to enable DP Master functionality. As for the manual and hopefully everythig else there is to know please grab a copy of the ET 200 Distributed I/O System manual (see chapter 9 and 10 as per THIS link). I hope this helps |
Cheers |
|
This contribution was helpful to1 thankful Users |
8/13/2014 8:43 AM | |
Joined: 5/9/2008 Last visit: 5/24/2024 Posts: 20 Rating: (0) |
Thanks very much!Your help is very helpful. |