Hello, In general it seems
possible, but accordig to the FAQ (https://support.industry.siemens.com/cs/ww/en/view/17660809)
the CP5711 isn't able to support direct data exchange, what is necessarry, even
if it will not receive/send any data itself. As alternative you maybe can think of using PROFIBUS for control the drive and using CBE20 with SINAMICS Link for data exchange between the CUs. Depending on your needs you can run drive control (via PROFIBUS) or SINAIMCS Link in isochronous mode (p8812=1). The "Parallel operation of communication interfaces" as well as SINAMICS Link with DCM are described in manual https://support.industry.siemens.com/cs/ww/en/view/109763559 |