Dear All, I have to connect 2 wire pressure transmitter with analog input module 6ES7 331-1KF01-0AB0 ,the output of transmitter is 4-20 mA ,the transmitter will take power supply from this module.anybody can please tell me the the correct configuration for this subject, Splitted from Overflow problem in AI module(6ES7 331-1KF01-0AB0). |
Last edited by: O_Moderator at: 5/12/2010 4:03 PMnew subject after splitting |
|
5/12/2010 4:19 PM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (309)
|
Hello Shaharyar,
I'm sorry this is not possible. The 1KF01 module can't supply transmitter with 17 or 24VDC. You will need external supply for this 2 wire transmitter and the connection should besimilar towhat you can see inthe manual of S7 module data, page 299 (CH5). Best regards. H-H |