4/23/2012 7:42 AM |
|
Posts: 211 Rating:
|
Martin,do not post questions here. Make a new thread. |
4/24/2012 11:20 AM | |
Joined: 12/1/2009 Last visit: 3/19/2023 Posts: 669 Rating:
|
Dear Martins_Eng, here is the solution: https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&objId=39334504&objAction=csOpen&nodeid0=41885258&lang=en&siteid=cseus&aktprim=0&extranet=standard&viewreg=WW Regards. |
Give us your feedback and show us your respect! |
|
4/24/2012 11:31 AM | |
Posts: 12 Rating:
|
Hello Martins_Eng, Use don't need to convert a 4-20mA signal to 0-20mA. Use the 0-20mA channel to read the 4-20mA signal. Take a look to the tuturial that I attached to this post (Analog Value Processing). AttachmentEN_M05_S7-1200_analog.pdf (542 Downloads) |
This contribution was helpful to
1 thankful Users |
4/25/2012 12:57 PM | |
Joined: 9/23/2005 Last visit: 3/13/2023 Posts: 4180 Rating:
|
Hi, you can found also ready to use blocks to your case in /tf/WW/en/Posts/31698#top |
Denilson Pegaia |
|
This contribution was helpful to
1 thankful Users |
5/17/2012 6:25 PM | |
Joined: 7/17/2010 Last visit: 7/26/2022 Posts: 184 Rating:
|
Thanks guys |
Follow us on