Hello GNC61 your receive data as nominated by "RECV" input of FC "DP_RECV" is too short. Since your drives I/O address starts at 560 and ends with 563, you need to nonimate at least a byte lenght of 564 for the "RECV" input of FC "DP_RECV" (or alternatively start your drive I/O address at 0). I'd also suggest you use a dedicated DB for this purpose instead of the Process Image. I hope this helps and have a look too at the FAQ What should you watch out for when configuring a CP342-5 as DP master and why is it necessary to call the FC1 "DP_SEND" and FC2 "DP_RECV" functions in the user program of the CPU in order to transfer data? which has more details on this matter. |