Hello iion; It would appear that one or more of the As-i slaves is not properly configured, often this could be an addressing error. Any active error LEDs on any of the slaves? Have a look at the conditions that make the Config error LED light up, in the screenshot below. Sinec S1 Master modules CP 2433- Siemens AG This manual also shows you how to read the address LEDs to know which slaves are active on the bus, and how to use the AS-i master to replace the address of a failed slave on a new module. Hope this helps, Daniel Chartier |