10/1/2012 12:27 PM | |
Posts: 3609 Rating: (29) |
Import of a Technical Question of the User YoursGold
|
10/1/2012 2:56 PM | |
Joined: 9/27/2006 Last visit: 6/5/2024 Posts: 12260 Rating: (2670) |
Hello YoursGold; This is probably not the answer you would have prefered, but: The newer version of the CP 342-5 (6GK7342-5DA03-0XE0) is also not DPV1-enabled (from the Siemens Industry Mall; see the Technical Specifications section): https://support.automation.siemens.com/WW/llisapi.dll/42319858?func=cslib.csinfo&objId=42319858&objAction=csView&nodeid0=10805985&lang=en&siteid=cseus&aktprim=0&extranet=standard&viewreg=WW&load=treecontent&prodLstObjId=4088948&subtype=130000 And based on the following table, you have to change to a CPU with an integrated DP port (such as the CP 313C-2DP)if you wish to use DPV1 services. Which SIMATIC S7 masters support the PROFIBUS DPV1 additional functions? Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 10/1/2012 5:17 PMLast edited by: dchartier at: 10/1/2012 2:58 PM |
|
This contribution was helpful to1 thankful Users |
10/9/2012 6:35 AM | |
Posts: 11 Rating: (0) |
Hi, 1. I used only read FC, since I don’t want to write / dig / control. 2. When I connected, my Bus is OK in NCM also it is saying “Slave polled my Own Master” 3. But the slave looks dimed out, & no read is happening. Attachments: HW Configuration online snap & NCM Slave Dig. Snap AttachmentOnline Snap.pdf (61 Downloads) |