4/16/2015 2:19 PM | |
Posts: 10 Rating: (0) |
Hello to all, I have found In several PLCs in my plant a similar issue. I have a 1214 DC/DC/DC v4.0 (214-1AG40-0XB0) with three modules connected: first (the closest to the PLC) CM1241 RS485/422 (1CH32), next CM1241 RS232 (1AH32), last CM1241 (1CH32). I have the message error: 9 of 50; Event ID: 16# 02:4042 CPU error: Hardware configuration error : Removal of hardware component not permitted CPU changes to STOP mode, new startup inhibit set: .. - System request for power cycle SCADA (RS422/485) Incoming event 4/15/2015 5:41:34.554 PM This error makes reference to the last CM1241 module. After this error the diagnostics buffer gives me a Firmware Error (ID16#02:401A): 8 of 50; Event ID: 16# 02:401A CPU info: Serious firmware exception (not relevant for user, system code: 16#00644A4E 16#10000034 16#030D0000) CPU changes from STOP (initialization) to DEFECTIVE mode AXONE_v2_ChemikBox Incoming event 4/15/2015 5:41:37.589 PM and the PLC goes to stop (4/15/2015 7:19:02.944 PM): 7 of 50; Event ID: 16# 02:4002 CPU info: Power off When it turns on (06/04/2015 22:42:39.124): 6 of 50; Event ID: 16# 02:4001 CPU info: Power on
it gives me and error to load the remanent memory: 5 of 50; Event ID: 16# 02:4009 CPU info: Retentive data error: No retentive data Current CPU operating mode: STOP (initialization) AXONE_v2_ChemikBox Incoming event 4/15/2015 7:19:27.976 PM After this the PLC start to work corectly (except the loose of the remanent memory). What is the origin of the problem? The program is designed in TIA Portal V13 and edited in V13 Sp1 upd1 (not upgraded to last udpate). Thanks.
----------------- |
Last edited by: samvaz at: 4/16/2015 5:32:29 PMLast edited by: CS Moderator at: 4/18/2015 4:53:27 PMnew subject after splitting |
|