5/17/2020 5:54 PM | |
Posts: 21 Rating:
|
Attachment20200516_145413.avi (80 Downloads) |
5/17/2020 6:01 PM | |
Joined: 2/5/2013 Last visit: 8/7/2024 Posts: 320 Rating:
|
Hi ABDO_2011, Thanks for you information, Activity 1 1.From Top Menu-->>Select Online --->> Upload device as new Station 2.Upload backup.(You need TIA 13 update 9) 3.Check Device View (Online Mode) Take Screen Shot 4.Select Controller and Press Ctrl+D (Online & Diagnostics)\ 5.Bottom Side Diagnostics buffer Select Save as Option & Save diagnostics buffer data. Activity 2 1.Open Final Commissioning backup 2.Check Device View (Online Mode) Take Screen Shot 3.Select Controller and Press Ctrl+D (Online & Diagnostics)\ 4.Bottom Side Diagnostics buffer Select Save as Option & Save diagnostics buffer data. Observation from you attached screen shot Hardware components HW_ID 273 is missing check particular ID for respective components from System component tab. |
Please rate it. |
|
This contribution was helpful to
1 thankful Users |
5/17/2020 6:08 PM | |
Joined: 2/5/2013 Last visit: 8/7/2024 Posts: 320 Rating:
|
Hi ABDO_2011, One more thing power off the PLC Panel. I think Signal Modules SM 1221/1222/1234 which are at right site of PLC are loosely connected to PLC. You need to check manually one by one,connect it properly to PLC. Br, AmolG |