5/25/2013 4:35 PM | |
Joined: 4/22/2010 Last visit: 10/17/2024 Posts: 5697 Rating: (715)
|
Hello, Although it's possible to save data to internal Eprom, i would recoment to use a memorymodule i.e. SIMATIC S7, MEMORY MODULE
Writing log to internal Eprom will cause to mutch write actions and wreck the Eprom verry quickly. Use the buildin Datalog function. Regards, Marcjan |
Problem solved? |
|
5/25/2013 8:38 PM | |
Posts: 103 Rating: (0) |
thanks for reply marcjan,and also confirm me is it possible to get data log from plc with ppi cmmmunication cable in s7 200 explorer. |
5/29/2013 7:13 AM | |
Posts: 103 Rating: (0) |
thanks marc |