hello, with the new MMC is the CPU "empty". You must set the IP-adress with Simatic Manager. PLC -> Edit Ethernet Node and search for MAC-adresses. Regards
André Räppel --------------------------------------------------------------------------------- www.raeppel.de work faster withinnovative PLC-Tools |
8/10/2009 2:10 PM | |
Posts: 88 Rating: (0) |
I know this method but it did not work. also with old MMC, I tryed to search mac addres with edit ethernet node, but could not find any mac address... |
8/10/2009 2:19 PM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
are you directly connected to PLC? Crossover patch cable? Regards
André Räppel --------------------------------------------------------------------------------- www.raeppel.de work faster withinnovative PLC-Tools |
8/10/2009 2:25 PM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
OK, which setting for the interface? ISO Ind. Ethernet or TCP/IP? Regards
André Räppel --------------------------------------------------------------------------------- www.raeppel.de work faster withinnovative PLC-Tools |
8/10/2009 2:26 PM | |
Posts: 88 Rating: (0) |
TCP-IP is selected. PG-PC interface settings ok... |
8/11/2009 1:33 PM | |
Joined: 5/26/2007 Last visit: 9/25/2024 Posts: 127 Rating: (3) |
why don't you download you whole config and program using dp first? after that i am sure you could access it with pn. |