5/20/2014 2:04 PM | |
Joined: 2/7/2013 Last visit: 6/28/2024 Posts: 4 Rating:
Hi I am a newbie to siemens and the CPU I am working on is showing SF with error "User interface (OB or FRB) not found" the event ID is 16#35A1. Looking for answers to rectify this error. attached is the Diagnostic buffer of module CPU 315-2 PN/DP. AttachmentDiagnose.zip (86 Downloads) |
5/20/2014 2:18 PM | |
Joined: 1/28/2009 Last visit: 7/11/2024 Posts: 6844 Rating:
As online manual suggest for event ID " 16#35A1" , You need OB40 in your program and download it to the CPU.The reason may come from the hardware interrupt from input/outputs.Check the hardware configuration and write program in OB40 to get more information regarding the interrupt.Read more here:
AttachmentHD_NEU.pdf (115 Downloads) |
5/20/2014 2:45 PM | |
Hi hdhosseini Tnkx for your quick response. I have downloaded the OB40 in the CPU, but the SF remains there. with same diagnose. I have checked the HW configuration as well and its correct. The CPU is working fine from past 2 months and yesterday it suddenly goes into Fault mode. Regards, SAM |
5/20/2014 3:08 PM | |
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating:
Hello, try to put also OB80, OB82, OB86, OB121, OB122 |
My last suggestion would be visually checking your Slaves and I/O modules for fault indication.Then open you hardware configuration editor then "STATION-->Open Online".Check the online veiw with graphical representation of ststus of each modules and some diagnostic information related.If possible save the buffer again, upload it here for further investigation!
This is all I can share! |
5/20/2014 4:40 PM | |
Joined: 11/14/2008 Last visit: 5/6/2024 Posts: 504 Rating:
Could be useful maybe ? in this document you can find back a lot of possible error codes with their possible remedies...
AttachmentSTEP7_ErrorCode_e.pdf (165 Downloads) |