9/4/2020 2:55 PM | |
Joined: 9/27/2006 Last visit: 7/12/2024 Posts: 12268 Rating:
Hello Asad; I hope you have no major trouble developing your Failsafe program, but it will require a bit of reading and dedication if you want to make the process as smooth as possible: First point, you will need an F-systems license to configure and program the failsafe operations, the RT license comes when you want to control the failsafe program on the CPU. The following Product Note will give you the required part numbers for the F-Systems licensing, and required software environment: S7 F Systems V6.2 Released for Delivery https://support.industry.siemens.com/cs/es/en/view/109740650 I recommend you take the weekend to study the contents of the following documents, to give you a good understanding of Safety programming procedures on a S7 CPU. - SIMATIC Industrial Software Safety Engineering in SIMATIC S7 (addresses both Distributed Safety and F-System programming packages) https://support.industry.siemens.com/cs/ww/en/view/12490443 - SIMATIC Industrial software S7 F/FH Systems - Configuring and Programming https://support.industry.siemens.com/cs/ww/en/view/101509838 - SIMATIC Process Control System PCS 7 Compendium Part B - Process Safety (V8.2) https://support.industry.siemens.com/cs/ww/en/view/109739339 Last point: the ET 200SP offers failsafe analog input modules, see the screenshot below. You can access the Et 200 page through this link, then open the I/O systems tab: Hope this helps, |