12/7/2010 3:48 PM | |
Posts: 2348 Rating: (264) |
Please upload diag buffer - really hard to see something on that picture. |
12/8/2010 12:27 AM | |
Joined: 10/7/2005 Last visit: 10/14/2024 Posts: 3024 Rating: (1054)
I agree with Aretand can for now only add the error description for your Event ID 4xE7 (don't forget to use the"Help on Event" button in he Diagostic buffer): The standby CPU has aborted its link-up/update and switched to STOP mode or DEFECTIVE mode. (The exact cause of this is listed in the referenced event of the partner CPU.) The H system continues to run in solo mode. |
Cheers |
12/15/2010 7:34 AM | |
Posts: 37 Rating: (0) |
Aret said right, send me the CPU buffer and I will tell you what happened |
12/16/2010 9:43 AM | |
Posts: 947 Rating: (45) |
See (check)indicator on sync modules. all must light. may be 1 sync modul or optocable is fault |
12/22/2010 9:29 AM | |
Joined: 12/7/2010 Last visit: 7/25/2024 Posts: 3 Rating: (0) |
Sorry for the delay!
AttachmentDiagnose.pdf (250 Downloads) |