Hello oms, I guess you are talking about a software redundancy solution. Referring to software redundancy manual(Page 26) the return value (error code) W#16#8014 means
Read the status word in redundant mode just to make sure that redundant link is working. When both CPUs are in RUN, it doesn't consequently mean that redundant link is established correctly. The only way to check it is the status word. You should also keep your eyes on the IM153-2 and check that they are switched correctly according to master CPU. Regarding communication to other masters. I do recommend to check software redundancy solution first and solve its problem without having communication jobs loaded on CPUs. Once you solve redundancy problem and make sure it's working well, you can start downloading your communication blocks and investigate other problems. Best regards. H-H |