12/17/2015 9:12 AM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello, please attach a screen what exactly is found! In the first post you write that nothing is found, in the second you write it is found. The GSD can not be the problem if the Slave is not found in accessible nodes! Which Address you have set on the Switches for DO Adress on the CU ? The GSD Files you can download here: https://support.industry.siemens.com/cs/ww/en/view/23450835 The FW V4.7 you can download here: https://support.industry.siemens.com/cs/ww/en/view/92554110 Regards Chtristoph |
Last edited by: ChristophD at: 12/17/2015 9:14:28 AM |
|
12/17/2015 9:53 AM | |
Posts: 35 Rating: (0) |
Hi, Sorry for not giving you a good explanation. My bad. My step on doing it. 1. Use the CU240E-2dp GSD v4.6, the drive station is appear. Use the CU240x-2DP GSD v4.7, the drive station is not appear. 2. Using the CU240E-2DP. CPU profibus address set to 10 and drive profibus address set to 1. 3. Compile and download the hardware. 4. Open the starter commisioning software, check the accessible node and found the profibus address for cpu and drive. 5. try to connect to select target, select the G120 drive. The error came out. Set PC/PG -> Profibus 1.5mbps. Drive switches I set it as 1. I have checked on the parameter for the switches address it is 1. Simatic manager v5.5 Starter version is 4.3.3 component SSP sinamics v4.6 installed Thank you. AttachmentPhoto.rar (71 Downloads) |
12/17/2015 10:59 AM | |
Posts: 35 Rating: (0) |
Hi.. In the attachment file is the pictures for the setting but I am not sure is it the one that you are asking for. Thank you so much. Best Regards, AttachmentPhoto1.rar (77 Downloads) |
12/18/2015 9:01 AM | |
Posts: 35 Rating: (0) |
Hi, Sorry for very late reply. My CU hardware is v4.7 but inside the accesible node it is written that my v4.7 is not installed. Do you have some sample for ladder programming to send data to the drive. Something like set the setpoint. Seems like the one I tried is not working maybe wrong. Thank you so much. Best Regards, Riko
Attachmentv4.7 is not installed.rar (103 Downloads) |
12/18/2015 9:37 AM | |
Joined: 5/12/2006 Last visit: 5/14/2024 Posts: 22251 Rating: (2985)
|
Hello, ok thius FW is not supported with the Starter V4.3.3, you should install latest STARTER V4.4 SP1 HF. In V4.4 SP1 the SSP for this FW is included: https://support.industry.siemens.com/cs/de/en/view/26233208 Application examples you can found here: https://www.automation.siemens.com/mc-app/sinamics-application-examples/Home/Index?language=en Regards Christoph |