10/22/2022 8:29 AM | |
Joined: 3/14/2008 Last visit: 7/12/2024 Posts: 2076 Rating:
|
Hi, if the block is completely new, then you can just download with a change and no stop is needed. If the block already exists and you add or remove IO or adjust default value for a IO or add a static variable, you can only download with a stop (except if you have a CPU410). If you only change logic or add a temp value in the stl, you can download change as well. The CPU410-5H is a PCS7 only CPU and allows download change almost all changes to existing blocks. For firmware <v8.2 you can only download in stop when default value of an IO is changed or changes to IO that is used in messaging (ALARM_8P). As of firmware v8.2, only changes to messaging must be download in stop. |
If I could help you, you can use the RATE button. Thank you. |
|
10/22/2022 2:36 PM | |
Joined: 3/14/2008 Last visit: 7/12/2024 Posts: 2076 Rating:
|
Correct. |
If I could help you, you can use the RATE button. Thank you. |
|