Hi, which errorcode is shown? A090 is not an error, it's only a status information. It means that there is no valid license. But: The communication works also without a valid license. A090 is shown and the SF LED is flashing (and there are entries in the diagnostic buffer), but the communication is possible. To get the registration key for your CPU, send the filled registration formto it4.industry@siemens.com. Wüstenräuber |
12/27/2012 11:15 AM | |
Posts: 3093 Rating: (323)
|
Yes, it is possible to fetch data from a PAC3200 without having a licensed Modbus block. Regards, Kaulquappe |
12/29/2012 7:28 PM | |
Joined: 3/21/2006 Last visit: 12/2/2024 Posts: 10229 Rating: (1181) |
Concerning A090 -What are the differences between the licensed version and the downloadable demo version of the blocks for Modbus TCP?So, this is not problem as has been mentioned before. id parameter in DB parameterMODBUS-PARAMhas to beidentical with correspondingConnection ID configured in NetPro. Best regards, Hristo Mihalev |