4/10/2014 6:25 AM | |
Posts: 1 Rating:
|
Hi, We use G120 with a 37kw PM for a water pump motor of 37kw. It gives F30002 when we raise the frequency from 30Hz to 47Hz by IOP hand mode. When we use a 45kw PM instead of the 37kw PM, the problem gone. The (DC link volt vs Time) graphs are attached. I want to keep using the 37kw PM by trying to rise DC link voltage threshold value (p2172). Would it cause any danger?
AttachmentF30002.pdf (733 Downloads) |
4/10/2014 3:02 PM | |
Joined: 10/11/2006 Last visit: 7/23/2024 Posts: 5877 Rating:
|
Hello, this is a typcial issue for the customer support: In Germany: Tel: +49 (0) 911 895 7222Fax: +49 (0) 911 895 7223 E-Mail: Online Support : http://www.siemens.com/automation/service&support Support Request : http://www.siemens.com/automation/support-request |
With best regards, |
|
1/8/2018 6:16 PM | |
Joined: 1/31/2014 Last visit: 7/23/2024 Posts: 6 Rating:
|
Hello I have replace master drives with the pm230 with a CU240 6SL32101NE232UG1 on a 15hp motor. I am seeing similar results. As the HZ increases the busvoltage is also increasing. It will trip on overvoltage at 60hz. I have a 30 hp drive that is doing the same thing but I have been able to keep it stable for now. I have never seen the bus voltage swing like this. The motor I am having the most trouble is free spinning not coupled to anything. The bus voltage will peak at 800 and then dip to 540. any thoughts? Thank you AttachmentF30002a.pdf (239 Downloads) |
1/9/2018 9:26 PM | |
Joined: 1/31/2014 Last visit: 7/23/2024 Posts: 6 Rating:
|
Yes tried everything you have mentioned, it has a line reactor and it will run fine without reactor? why is the line reactor causing distortion/ noise on the dc bus.AttachmentF30002a.pdf (251 Downloads) |
Follow us on