9/24/2021 10:21 AM | |
Posts: 23 Rating: (5) |
Hello, Have you installed "Quality Update" package for Desigo CC 5.0 / 4.2? Desigo CC V5.0: products family Quality Update 1 - ID: 109800951 - Industry Support Siemens BR Robert |
9/24/2021 10:29 AM | |
Joined: 6/4/2010 Last visit: 9/13/2024 Posts: 387 Rating: (128)
Dear forum member, There is a known issue for all the Desigo CC V4.x and V5.0 versions. You have to install the Quality Updates or patches, depending on the version. Please read this FAQ “Desigo CC V4.x: Desigo PX System 6.3 controllers cannot be imported” for further details: https://support.industry.siemens.com/cs/ww/en/view/109802397 (this is for Siemens engineers and authorized Solution Partners only. Please contact your local Siemens SI BP representative, in case you do not have access to the Extranet). Newer Desigo CC versions like Desigo CC V5.0 QU1 and later already support BACnet Revision 1.15 for PX controllers out of the box. Please note that generic (third party) BACnet integrations are not affected from this problem. Best regards, Albis |
9/24/2021 4:00 PM | |
Posts: 18 Rating: (2) |
Thank you all, with your support I solved the problem. |