2/26/2024 4:32 PM | |
Joined: 7/7/2010 Last visit: 5/17/2024 Posts: 14751 Rating: (2374)
|
I may be wrong, but once you enable the HSC for Ch 0 & 1 with the checkbox, you then carry out the configuration in the DI module, at each Ch 0 & 1's Properties -> General. Refer to this link: Count - SIMATIC S7-1500/ET 200MP Digital Input Module DI 16x24VDC HF - ID: 59193001 - Industry Support Siemens
|
science guy |
|
2/26/2024 4:38 PM | |
Joined: 1/28/2023 Last visit: 4/5/2024 Posts: 45 Rating: (1) |
The issue is I can not configure HSC block as per picture attached. Its configuration sequence doesn't see PLC local modules. That's the point! |
2/26/2024 5:32 PM | |
Joined: 7/7/2010 Last visit: 5/17/2024 Posts: 14751 Rating: (2374)
|
That linked document tells you not to try because it is not intended to work as a TO. FYI, that is where I found the link I previously posted. I read it and knew it was directly applicable to your situation. Delete your TO and then look at this document. Personally, I find the document lacking, so looked into the same document and located the much needed piece of information (at least to me): https://support.industry.siemens.com/forum/us/en/addpost/313269/?quotedPostId=1192165 In there, it shows how to get the HSC(s) to work, and where to look for the count value(s).
|
science guy |
|
This contribution was helpful to1 thankful Users |
2/27/2024 6:50 AM | |
Joined: 1/28/2023 Last visit: 4/5/2024 Posts: 45 Rating: (1) |
It seems you are right. But it doesn't make me happy. Either I need Compact version of plc or I need an adequate application example in terms how to use DI HF modules for HSC. Because in Chapter 5.2 of document as above I understood almost nothing. |
2/27/2024 7:07 PM | |
Joined: 7/7/2010 Last visit: 5/17/2024 Posts: 14751 Rating: (2374)
|
Maybe this library and the documentation that comes with it may be useful. I know it would be for me. https://support.industry.siemens.com/cs/document/109482396 and this one (which is how I found the above link): https://support.industry.siemens.com/cs/products/6es7521-1bh00-0ab0
|
science guy |
|