Hello! Faced with the problem of a lot of errors. simotion d425-2 simotion SVT error no:20005 Sinamics STV error:1651 Sinamics STV error:1800 I ask for help in troubleshooting. I don't understand where to drip. Rebooting doesn't help. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/18/2024 11:30:27New subject after splitting |
|
3/18/2024 9:43 AM | |
Joined: 10/11/2006 Last visit: 10/9/2024 Posts: 5910 Rating: (808)
|
Hello, your offline hardware topology doesn't fit to your online configuration. Please solve this problem. Easiest way would be to do a factory reset and do automatic drive configuration again. F01800 (A) DRIVE-CLiQ: Hardware/configuration error Cause: A DRIVE-CLiQ connection fault has occurred. Fault value (r0949, interpret decimal): 100 ... 107: Communication via DRIVE-CLiQ socket X100 ... X107 has not been switched to cyclic operation. The cause may be an incorrect structure or a configuration that results in an impossible bus timing. 10: Loss of the DRIVE-CLiQ connection. The cause may be, for example, that the DRIVE-CLiQ cable was withdrawn from the Control Unit or as a result of a short-circuit for motors with DRIVE-CLiQ. This fault can only be acknowledged in cyclic communication. 11: Repeated faults when detecting the connection. This fault can only be acknowledged in cyclic communication. 12: A connection was detected but the node ID exchange mechanism does not function. The reason is probably that the component is defective. This fault can only be acknowledged in cyclic communication. Remedy: For fault value = 100 ... 107: - ensure that the DRIVE-CLiQ components have the same firmware versions. - avoid longer topologies for short current controller sampling times. For fault value = 10: - check the DRIVE-CLiQ cables at the Control Unit. - remove any short-circuit for motors with DRIVE-CLiQ. - carry out a POWER ON. For fault value = 11: - check the electrical cabinet design and cable routing for EMC compliance For fault value = 12: - replace the component involved. https://support.industry.siemens.com/cs/ww/en/view/109827046 |
Last edited by: Jen_Moderator at: 03/18/2024 11:32:58Text formatting optimized. With best regards, |
|
Follow us on