3/18/2014 7:08 PM | |
Posts: 3 Rating: (0) |
Hi All, Is there no one who can help me? All help is appreciated |
3/18/2014 7:59 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715) |
Hello, I think you should have a look at this manual: SIMODRIVE 611 digital Drive Converters In chapter 10 you can see that pin 56 and pin 14 are analog input 1 Because it's a bipolair input there is no reference 0 to + 10V is speed in direction forward, 0 to -10V is speed in direction backward. +- 10 volt signals usualy are generated by analog card in PLC. Regards, Marcjan |
Last edited by: Marcjan at: 3/18/2014 8:01 PMProblem solved? |
|
5/22/2014 2:26 PM | |
Posts: 17 Rating: (1) |
Hi, Please findattached the details.... Terminal 56 & 14 are analog setpoint signals. If you test in open loop then you may have to use battery of 1.5V between terminal 56 & 14. Regards, Santosh Attachment611 analog Start-Up Guide.pdf (191 Downloads) |
5/27/2014 4:22 PM |
|
Joined: 10/10/2010 Last visit: 10/7/2024 Posts: 307 Rating: (15) |
you can use a variable Dc source for setpoint , try the potentiometer for setpoint change |