Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi engco, not sure what you want to do, but try to do it with HW- or SW-gate. regards |
FCK WAR! |
|
8/15/2016 9:42 AM | |
Joined: 2/2/2016 Last visit: 2/8/2023 Posts: 221 Rating: (2) |
i want hsc to count normally but stop count when i0.4 is on. |
8/15/2016 10:13 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi enco, okay, I was afraid to see, that the S71200-PLC counters have no Gates. But a solution could be: Save the counter-value with a rising edge of I4.0 and write it back in the counter with a falling edge of I4.0. And copy the counter value to an other MD or DB when I4.0 is not true. And from this MD or DB you use the counter value. Have a look in the S71200 System Manual, chapter 10.1 how the counter control instructions work. hope this helps, regards, |
FCK WAR! |
|
8/15/2016 10:49 AM | |
Posts: 5225 Rating: (1195)
|
Use the same idea as listed [ link ] to save the HSC value. Instead of a power outage, you will have %I0.4 as an event. |
8/15/2016 11:47 AM | |
Joined: 2/2/2016 Last visit: 2/8/2023 Posts: 221 Rating: (2) |
do you mean power stage in step 9 ? how to insert i0.4 |
8/15/2016 1:28 PM | |
Joined: 2/2/2016 Last visit: 2/8/2023 Posts: 221 Rating: (2) |
where should i put I0.4, I tried cut the power and it saved it. |