8/13/2024 6:04 AM | |
Joined: 3/11/2019 Last visit: 11/8/2024 Posts: 1653 Rating: (305)
|
Hi, D_ACT_DP can only be used to deactivate the whole io-device, but not submodules. As already mentioned, option handling (configuration control) is what you are looking for. There is also an FAQ: Configuring standard machines in TIA Portal (configuration control)What should you watch for with configuration control (option handling) with fail-safe controllers S7-1200 and S7-1500?regards sancruz |
Feedback appreciated, please rate |
|
This contribution was helpful to1 thankful Users |
Follow us on