Hi Everyone, I am facing some short circuit error in DO Module of safety system (FDO10). This error is not coming continuously but often found when some download takes place. I have attached screenshot. Can anyone advise what will be the cause for this error. What action I can take to overcome this error? Thanks in Advance, GJ AttachmentESD Module Error.pdf (55 Downloads) |
11/24/2016 3:47 PM | |
Joined: 4/8/2016 Last visit: 10/1/2024 Posts: 133 Rating: (45) |
Hey GJ, Have you checked the wiring of the affected channels? The Installation and operating manual might help you: https://support.industry.siemens.com/cs/ww/en/view/19026151 What is connected to the affected channels? I could imagine that the reason for the detected short circuit is a too high current which might be caused by a capacitive or inductive load. |
Last edited by: 51N3P at: 11/24/2016 3:47:20 PMKind regards |
|
This contribution was helpful to1 thankful Users |
11/25/2016 4:00 PM | |
Joined: 4/8/2016 Last visit: 10/1/2024 Posts: 133 Rating: (45) |
If you checked the wiring and everything is according to the manual I do not have a specific idea at the moment. But nethertheless I would disable the spare channels in the HWConfig if they are not needed to avoid errors. And I found another Forum entry with a similar problem: https://support.industry.siemens.com/tf/ww/en/posts/solved-external-short-circuit-with-f-do-card/153796/?page=0&pageSize=10 |
Kind regards |
|
This contribution was helpful to1 thankful Users |