6/18/2011 8:02 AM | |
Posts: 8946 Rating: (999) |
Why there is no slave 77 in your sketch? First thing to to, like always, is to check cable and plugs ect.... Give us the Programm, at least HW-config. |
6/18/2011 12:48 PM | |
Posts: 947 Rating: (45) |
I think the configuration is not considered OLM (or it influence). |
6/20/2011 3:36 PM | |
Posts: 14 Rating: (0) |
I'm sorry "IBN-Service", the node 77 is not in the drawing because the node was inserted after the making of the drawing. Attached the two requests: We appreciate the help. AttachmentFile.zip (93 Downloads) |
6/20/2011 4:27 PM | |
Posts: 1547 Rating: (129)
|
Hello Eduardo Bannwart, I found thefollowing message several times in the diagnostic buffer: 118 22:47:15:818 03.07.1994 PROFIBUS LAYER 2 |
Last edited by: Rated X at: 6/20/2011 4:28 PMtypo |
|
6/20/2011 9:49 PM | |
Posts: 14 Rating: (0) |
Thanks for the reply: Replies: Unlikely terms reversed the cables, they are physically isolated. I've checked several times the terminators. Today I will switch back terminators for two new terminators. We have no problems in the Master System 6. Signs of this extension is not falling. The message below may be the problem? What is the reason for this message? "127! 16/07/1994 00:43:42:834 DP-Master Date record could not be written The record date could not be written to slave slot 9 of 11. Error: 0x80A2. " |
6/22/2011 6:53 AM | |
Posts: 8946 Rating: (999) |
It depends. Pleas read first the basic beginner manuals. You will find a lot of links here. |