2/3/2011 2:06 AM | |
Joined: 9/27/2006 Last visit: 9/16/2024 Posts: 12282 Rating: (2683) |
Hello Rick; You are over-complicating things, I fear. Once you have the DP/DP coupler setup in both DP-master projects, and you have noted the I/Oaddresses that will be used in each CPU,all you have to do is configure the salve module table (number and size of each data exchange) in the HWConfig of each PLC. For an example configuration, look at the following FAQ: http://support.automation.siemens.com/WW/view/en/19281019 Examine the 2 tables shown in the attached document in the FAQ. Notice that they correspond line-per-linein size, but that they are reversed in type: Outputs from the first table become Inputs in the second... Once the HWConfig has been compiled and downloaded to each CPU, the Dp/DP Coupler will start exchanging the data setup in these tables. It is up to you to Move data from/to these addresses to/from your PLC program. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 2/3/2011 2:08 AM |
|
2/22/2011 10:51 AM | |
Posts: 70 Rating: (3) |
Hi - thats correct. Another thing - the configuration must be 100% identical in both PLC's or else the DP/DP wont connect. /søren
|
2/22/2011 1:50 PM | |
Posts: 17 Rating: (0) |
Wha do you mean both have to be identical in configuration? |
2/22/2011 3:04 PM | |
Posts: 74 Rating: (2) |
Hello RickM, the term "both have to be identical in configuration" mean that You have to set I/O space size, order and adress composition same in HW Cfg of every one PLCs (2pcs). Would be better read DP/DP Coupler manual - page 40 and 41. Vitas Attachmentdpdpk_e.pdf (236 Downloads) |
2/22/2011 3:31 PM | |
Posts: 17 Rating: (0) |
what if the other PLC you connecting to using DP/DP coupler is not a Siemens PLC there address has to be the same? |
Follow us on