4/22/2018 7:06 PM | |
Joined: 4/1/2018 Last visit: 6/13/2022 Posts: 2 Rating:
Dear sir I Have to use 6RA8075-6DV62-0AA0 drive. But drive is running in jog mode in STARTER software display is wait for the voltage at 3U1, 3W1 and fault F60105 is occures So please help me to what problem is also ------------------------------------------------------------------------------------------ Attachment6RA80.zip (178 Downloads) |
Last edited by: Jen_Moderator at: 4/23/2018 8:21:58 AMNew subject after splitting |
4/24/2018 7:57 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating:
Hello, F60105 = Field current monitoring fault in field circuit. Have you set field related data correctly? Is line contactor ON? Is fuse in field circuit healthy? Please check fault value in r50047. Note for fault value = 1: r50047[1]: Setpoint at field current controller input (r52268) r50047[2]: Actual value at field current controller input (r52265) r50047[3]: External monitoring (p50265) r50047[4]: Operating mode (p50082) r50047[5]: Threshold for monitoring (p50396) Note for fault value = 2: - r50047[1]: line state (r53145). |