I have similar situation with this question. i have experience working with SFC Type combined with process tag type (PTT) in the PCS7 V8.1 (non Simatic BATCH) continous process. Now i have a project that need to be developed using PCS7 V9.1. This time i plan to use CMT instead of PTT, after i read the compendium C i realize now SFC type have evolved to two version either EPHT or EMT. After read the documentation and trying some prototype i still can't decide which better to choose in my situation. Because i will not utilize SIMATIC BATCH, what your suggestion for my situation ? Is it better i choose EMT / EPHT ? many thanks. ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 10/27/2021 07:11:01New subject after splitting |
|
10/27/2021 7:51 AM | |
Joined: 3/14/2008 Last visit: 11/18/2024 Posts: 2131 Rating: (953)
|
Hi, I highly suggest using the new concept EPHT/EMT. The concept is the new standard and the biggest advantage is the synchronization that is a lot better than with PTT. With PTT you can do bulk engineering, but when the Process Tags are created, synchronization is very limited, changes cannot be synced to the PTT ending up deleting the Process Tag and generate again, but all connections will get lost. The EMT/EPHT can be synchronized via a new editor called Plant Types (XMLTRANSFER). When a change is made like adding an And04 block to the EPHT/EMT, after synchronizing, the instance EPH/EM will get this And04 block as well. The EPHT/EMT can also be used with regard of Plant Automation Accelerator (since newest version). In EPHT/EMT you can add lower level EM as well, so if you have like a EPHT, you can control lower level EM as well which makes engineering very easy and enables a lot more options. Apart from this, CM can be controlled as well. In a CMT you can create commands like SetOpen and statuses like IsOpened to control a valve, you create a role in the EPHT/EMT and use the role to control the valve in the SFC. There like placeholders. After the EPHT/EMT is instanced, you can attach the real CM to the configured role and your done. An EPHT/EMT always has an SFC type, you can set the SFC to class: "EOP" or "EPH" in order to use it in SIMATIC BATCH, if you choose "None", it won't end up in BATCH, so BATCH is not necessary at all. |
Last edited by: Oreca at: 10/27/2021 07:53:10Last edited by: Oreca at: 10/27/2021 07:58:43If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
10/27/2021 12:49 PM | |
Joined: 3/14/2008 Last visit: 11/18/2024 Posts: 2131 Rating: (953)
|
Hi, if you have several EPHT it is even possible to control the same lower level EM, from different EPH. That is not possible if you have EMT that control lower level EM. Unfortunately Siemens confuses the user because they use name: EPH that is normally an equipment phase equivalent to the RPH in Simatic Batch. But doesn't have to be.. For the synchronization: Make sure you synchronize the SFC from the Charts folder and not from Blocks folder. Otherwise the synchronization will fail. The SFC can be updated through Charts->Update block types. After that you can synchronize the EPHT/EMT via Plant types of you have made any changes to the CFC of the EPHT/EMT. After that,
|
If I could help you, you can use the RATE button. Thank you. |
|
10/28/2021 8:43 AM | |
Joined: 3/14/2008 Last visit: 11/18/2024 Posts: 2131 Rating: (953)
|
Hi, You can easily convert from EPHT to EMT and vice versa by right clicking the object and hit convert in the TIO editor, but at the moment there is a bug that instances are not updated so all instances need to be done also..I hope they fix it soon. Please always work in the master library. Do not work on SFC in the project. Updating SFC block type must be done from the Charts folder in the master library to all projects resulting in a full compile and download change. To update the SFC type: select master library charts folder (Component View) and select the FB, go to Options->Charts->Update block types and execute the change. |
Last edited by: Oreca at: 10/28/2021 08:45:39If I could help you, you can use the RATE button. Thank you. |
|