8/4/2020 8:14 AM | |
Joined: 10/11/2006 Last visit: 8/16/2024 Posts: 5894 Rating: (803) |
Hello, it is possible to use 5.9.2 TM Count 1x24V / TM Count 2x24V or 5.9.3 TM PosInput 1 / TM PosInput 2 for TTL or SSI encoder. https://support.industry.siemens.com/cs/ww/en/view/109749262 Direct combination between S210 is not possible. You need a PLC. Configuring Technology Objects with SIMATIC S7 1500 and SINAMICS S210 in TIA-Portal https://support.industry.siemens.com/cs/ww/en/view/109749795 |
With best regards, |
|
Follow us on