1/17/2018 8:06 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (873) |
Hello Goran_, Please provide the drive complete MLFB number along with options installed. (If possible attach drive nam plate snap) Please provide motor complete MLFB number to understand the type of encoder installed in motor. Above information will help to understand the system based on which help can be provided. Check if separate encoder (apart from motor encoder) is installed to measure direct out put rotation/speed. HTH. |
1/17/2018 9:28 AM | |
Posts: 141 Rating: (0) |
Hi, here is the image of drive and motor plates. No additional hardware is installed in drive, no additional encoder. |
1/17/2018 11:48 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (873) |
Please confirm in whch slot FM 350 module is inserted & its address physical as well as programed. |
1/20/2018 10:31 PM | |
Posts: 141 Rating: (0) |
Here is an image of hw config, and SFB48 usage. |
1/20/2018 10:35 PM | |
Posts: 141 Rating: (0) |
And here is FM350 configuration |
1/21/2018 4:56 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (873) |
Hello SFB 48 which you programed is for compact CPU. Since you configure FM350 module you need to call FC & program FM module for counting. Please download manuals from below links for detailed information. FM 350-1 Counter Function Module Installation and Parameter AssignmentSIMATIC FM 350-1 First Steps in Commissioning |
Last edited by: PISCEAN 2010 at: 1/21/2018 5:20:48 AMLast edited by: Jen_Moderator at: 1/22/2018 11:26:10 AMInserted right links. |
|
This contribution was helpful to1 thankful Users |
1/21/2018 9:23 AM | |
Joined: 1/21/2013 Last visit: 6/2/2024 Posts: 4620 Rating: (705) |
Hello, also http://support.automation.siemens.com/WW/view/en/598197 you have to put in D position on the left of the card for 24V signal then in the program you have to call FC0 CNT CTRL and first call in your block tree the UDT and make a DB with UDT associated you find this block in the library of FM350. you will find your counter value in DBx.DBD34 |
Last edited by: Ste39 at: 1/21/2018 9:25:38 AM |
|
This contribution was helpful to1 thankful Users |