Good day. We got an error 025201 on the X-axis on our machine. A 6SN1123-1AA00-0CA1 power module with a 6SN1118-0NH11-0AA0 control board is installed on this axis. Is it possible to diagnose a malfunction, on the power module, to replace the 6SN1118-0NH11-0AA0 control unit with 6SN1118-0NH11-0AA1? Will the new control unit break from this? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 09/08/2020 13:06:55New subject after splitting |
|
9/9/2020 9:08 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, Your X axis is faulty & significance of 380500 fault code 607 is - X axis drive current controller output is limited. i.e. controller does not get feedback from axis to achieve command speed even though motor voltage is at its max level. So please check, motor winding with DMM, motor cable continuity, (if any phase missing), check DC bus voltage, check drive power LT module & if all found OK, replace one by one, drive power module first & if problem persist, replace drive control card. Please refer attached sheet which shall help you to check X axis drive power module. HTH AttachmentLT module checking tip.pdf (463 Downloads) |