4/4/2024 9:34 AM | |
Joined: 12/1/2023 Last visit: 4/19/2024 Posts: 7 Rating: (0) |
Hello, We want to re-purpose Simodrive motor controllers with the corresponding servomotors. The are installed in a CNC machine center which was equipped with a Heidenhain controller which is not functioning anymore. 2x Siemens 1FK6063-6AF71-1AG0 with encoder Heidenhain ERN 1381-2048 1x Siemens 1FK6101-8AF71-1AH0 with encoder Heidenhain ERN 1381-2048 1x Siemens 1PH7137-2NG02-0CA0 with encoder Heidenhain ERN 1381-2048 Simodrive E/R modul 6SN1145-1BA02-0CA0 - 36/47KW spindel Simodrive LT-modul 16A 6SN1123-1AA00-0EA0 X+Y as Simodrive LT modul 2x 50A 6SN1123-1AB00-0CA1 Z as Simodrive LT modul 80A 6SN1123-1AA00-0DA0 we have installed new 6N1118-0NH01-0AA1 boards Thank you for your support. Pascal Attachmentsiemens.pdf (96 Downloads) |
4/6/2024 1:39 AM | |
Joined: 10/17/2007 Last visit: 7/14/2024 Posts: 4008 Rating: (353)
Dear User, from your picture, I see you have error A040 instead of A080, I attached error explanation so You see the picture's function is important and from you picture I see you 611U control card with an option submodule --PROFIBUS Option module I am not sure what is the original wiring /connecting, but I see now that sub-module has red led and no cable connected to it. Hope I answered your question--the error is A040 AttachmentE_A040.pdf (118 Downloads) |
If you like my comments please |