2/10/2016 11:29 PM | |
Joined: 9/27/2006 Last visit: 5/21/2024 Posts: 12257 Rating: (2668)
|
Hello Sandrao; You must insert the GSDML file in the HWConfig before you do your upload. I have found the GSDML file in the following FAQ, I suggest you proceed with the download and execute the file, without proceeding with the firmware upgrade. Then proceed with your upload. https://support.industry.siemens.com/cs/ww/en/view/68349561 Hope this helps, Daniel Chartier |