Hello, So I have three S7 independentsystems (each have own projects): 1) CPU312 and CP343-1 Lean 2) CPU315-2DP and CP343-1 3) CPU315-2DP and CP343-1 They are wiredwith ethernet androuter. Need is: -transfer from 1) to 2) bit information, interger is enough, 16 bit -transfer from 1) to 3) bit information, interger is enough, 16 bit -transfer from 2) to 1) bit information, interger is enough, 16 bit -transfer from 3) to 1) bit information, interger is enough, 16 bit I have read several days manuals etc. but still I cannot understand completely how I must do this.. Siemens example projects are good but.. https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&objId=22867279&load=treecontent&lang=en&siteid=cseus&aktprim=0&objaction=csview&extranet=standard&viewreg=WW I think best theis use S7 connection and: USEND, URCV, BSEND, BRCV, GET, PUT. Whichof those is best? I don´t need tranfer time critical information.. How should I configure NetPro? In each project? My programmingcareer is just starting.. Self learning is efficient, but still I need some quide. |
1/28/2009 6:14 PM | |
Posts: 6 Rating: (0) |
|
1/29/2009 3:27 AM | |
Posts: 73 Rating: (20) |
Hi PLCS7USER, I would first check to see if the CPU and the communications portsupports S7 Client and S7 Server functionality. See the link http://support.automation.siemens.com/WW/view/en/17628518 and http://support.automation.siemens.com/WW/view/en/24352751 If you use the GET/PUT please make sure you use the correct ones. These blocks exist in two libraries. One is the Simatic Library and the other is in the Simatic Net library. They have the same FB numbers, same names but the length is different. |
1/31/2009 12:47 AM | |
Posts: 5822 Rating: (412)
|
Dear plcs7user, I am sorry but the use of the CP 343-1 Lean with S7-Communication will not work. This will at least not work at a PCL with the CP 343-1 Lean, as the CP would have to work as an active node within a S7-Communication. The CP 343-1 Lean is only able to be a S7-Server. |
Follow us on