7/14/2009 6:57 AM | |
Joined: 5/28/2008 Last visit: 8/6/2024 Posts: 4515 Rating:
|
Hello gre_m, No you do not need to make rewire. |
Ayman Elotaify |
|
7/14/2009 10:57 AM | |
Joined: 10/7/2005 Last visit: 8/9/2024 Posts: 3016 Rating:
|
Hello again gre_m again, the answer is: It depends. You can get away without rewiring and without the need for dummy modules if you re-arrange your ET200S (and HWconfig) as per attached picture. Assuming you have a bit of slack in the cables that are wired to the terminal modules you'd move/rearrange the terminal modules together with their corresponding electronic module. This way you avoid re-wiring and also the need for dummy modulesas you now have all "reserve" modules at the end of the station. Pleasemake sure to properly configure your "Option handling" which needs to be done for the Station (IM properties) as well as for the power module (power moduleproperties). I've never had the need to use Option handling and should you feel that you'd be better off without it, simply remove the 1,2,3modules all together. I hope this helps |
Cheers |
|
7/14/2009 3:35 PM | |
Posts: 947 Rating:
|
Hello fritz! For big station ET200s (~80cm long)this is equivalent"rewire". |
Follow us on