Dear Sir/Madam, I am new person, but I am very like profibus simoreg Siemens. Please instruction to me how to understand and communication between PLC Siemens and simoreg 6rA70 drive. At the confg of PLC, I set up drive with DP slave: PPO4, PZD-6/6 ( mean has 6 word) and address of drive assume: 112..123 I want to know the drive how to understand for start/stop, reference setpoint, feedback and K connector. Please help me and instruction me. Many thanks & best regards, Nguyen Duy Tam ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 7/2/2018 7:25:14 AMNew subject after splitting |
|
6/30/2018 10:21 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, You need to install CBP2 Profibus board on 6AR70 & need to define PPO type , bus address & enable profibus parameterization. Please refer the SIMOREG DC-MASTER 6RA70; software version 3.1 manual for detailed information. In PLC after selecting CPU you need to configure hardware & in project need to connect 6RA70 on profibus. Refer FD G180,181,182 & 183 you can transfer data by configuraing appropriate BICO parameters, e.g. control word 1 KK0030 you can connect Binnector to switch ON, enable pulse, enable RFG etc commands. Status word K0032 will send the status signals of drive like, drive is ready, OFF signalsapplied, if fault is active etc. etc. You can send reference main set point via PZD2 & drive actual speed value will be received via HIW. Like this user may transfer the process data. HTH. |
Last edited by: Jen_Moderator at: 7/2/2018 7:27:56 AMOptimized link. |
|
This contribution was helpful to1 thankful Users |
6/30/2018 10:38 AM | |
Posts: 2 Rating: (0) |
Dear Sir, Thanks for your support so much. I will make follow your instruction. Best regards, nguyen Duy Tam |
Follow us on