6/3/2019 12:58 PM | |
Posts: 17 Rating:
Hi "CPU 1513F-1 PN" With Remote IO "IM 155-6 PN ST" I have some errors on Safety Digital Output Module: 6ES7 136-6DB00-0CA0 |
Posts: 17 Rating:
Posts: 17 Rating:
3/18/2022 2:22 PM | |
Joined: 4/9/2021 Last visit: 5/22/2022 Posts: 2 Rating:
Hi, Are you able to solve this issue as I am facing the same issue? |
3/21/2022 9:22 AM | |
Joined: 3/11/2019 Last visit: 7/9/2024 Posts: 1511 Rating:
Hi, if the "f-address memory is not accessible", please check if the memory is available/plugged in. Depending on which hardware is used, the "f-address" memory is located on different locations. For an ET200SP the "f-address" memory is between the module and the baseunit. A picture can be found with following FAQ: What should you check when the F destination addresses cannot be assigned?On s7-1500 / et200mp modules, the f-address memory is in the front connector. There are pictures in the s7-1500 system manual. maybe this helps regards sancruz |
Last edited by: sancruz at: 03/21/2022 09:23:33Feedback appreciated, please rate |