3/17/2013 5:20 PM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181) |
Hello, You can use the Excel table "S7fcotia.xls" for calculating monitoring and response times in a safety-related application with S7 Distributed Safety. The table is available for free downloading in Entry ID: 25412441. The "S7fcotia.xls" table has three tabs. The first tab contains the calculation of the maximum runtime of the F runtime group depending on the F CPU used. Here, among other things, you enter the number of F function blocks used from the S7 Distributed Safety library. Best regards, Hristo Mihalev |
3/18/2013 3:03 AM | |
Joined: 10/7/2005 Last visit: 10/13/2024 Posts: 3024 Rating: (1054)
Hello Madhava I'm afraid to say I can't give you a specific answer on how to fix this, but have some hints: 1.) Check the thread F-Monitoring time where the same issue is also discussed 2.) Grab a copy of theSIMATIC Industrial Software S7 F/FH Systems - Configuring and Programming manual which contains more info onF-monitoring time. 3.) Grab also a copy of theSIMATIC Industrial Software Safety Engineering in SIMATIC S7 and see AppendixA4 for moredetails on F-monitoring times for an S7 F/H system. 3.) To calculate the times manually usethe "S7timeb.xls" excel workbookfrom SIMATIC S7 F Systems: Execution Times of Failsafe Software Blocks, Runtime of the F Shutdown Group, Monitoring and Response Times (Do NOT use "S7fcotia.xls" asitonly applicable for Distributed safety). I hope this helps |
Cheers |
3/20/2013 12:22 AM | |
Joined: 11/26/2011 Last visit: 6/29/2023 Posts: 508 Rating: (23) |
Thanks Fritz.. I will try to optimise monitoring time further. |