Hello Stevec; To configure and program a Safety solution for the s7-1500, you need the additional paclage Simatic Safety (6ES7833-1FB16-0YA5, see the order list in the second post below) https://support.industry.siemens.com/cs/ww/en/view/54110126 https://support.industry.siemens.com/cs/ww/en/view/109772968 Simatic safety F-Systems is approved up to SIL3 (CAT 4) applications, on condition that ypu resqpect the basic requirements, including the use of F-I/Os and F-communication blocks for all safeyty-related controls. You can configure and use standard (non-safety) I/Os in your configuration and in your program, but only for non-safety controls. Using standard I/Os for safety applications will never receive approval for SIL3. Have a look at the screenshot belw, taken from the Simatic safety manual proposed earlier. Hope this helps, |