5/25/2021 7:25 PM | |
Joined: 8/18/2017 Last visit: 3/7/2022 Posts: 1 Rating: (0) |
Hi there, we got same fault F0026. First we checked all basic parameters, & found all ok. After reset fault & test, we found same fault F0026 again. First we check CUVC card but its good. Finally we decide to check IGD card. there was a problem in backside of card. There is a capacitor leaked, that liquid make short circuit in other (near) leaking area. See the picture RED mark area. We replace card with new good one. After all assembly job check all parameter with PC. Found all ok, than start system try & TEST, its working smoothly, normal without any fault. Please check this board also, if you got fault on display F0025, F0026, F0027. Thanks for read. ------------------------------------------------------------------------------------------ |