Hello, Here is the diagnose file. There is no change on the problem. We take fault messages from different nodes almost 10 times a day. Here is the short example from the file. "I/O access error, reading" events related to "Distributed I/Os: station return" events. Thank you for your help. Diagnostic buffer of module CPU 319F-3 PN/DP Order No./ Description Component Version 6ES7 318-3FL00-0AB0 Hardware 3 - - - Firmware V 2.8.3 Boot Loader Firmware expansion A 10.3.3 Event 1 of 100: Event ID 16# 38C4 Distributed I/Os: station return Address of the affected DP slave: station number: 16 DP master system ID: 1 Log. base address of the DP slave: Input address: 8171 Log. base address of the DP master: 8190 Requested OB: Rack failure OB (OB86) Priority class: 26 External error, Outgoing event 08:47:41.075 AM 09/11/2018 Tehre are I/O access error, reading and writing events Event 8 of 100: Event ID 16# 3842 Module OK Module type: Distributed I/0s Input address: 8171 User information available Diagnostic interrupt from substitute Requested OB: Diagnostic interrupt OB (OB82) Priority class: 26 External error, Outgoing event 08:47:41.051 AM 09/11/2018 Tehre are I/O access error, reading and writing events Event 39 of 100: Event ID 16# 39C4 Distributed I/Os: station Failure Address of the affected DP slave: station number: 16 DP master system ID: 1 Log. base address of the DP slave: Input address: 8171 Log. base address of the DP master: 8190 Requested OB: Rack failure OB (OB86) Priority class: 26 External error, Incoming event 08:47:41.007 AM 09/11/2018 Event 40 of 100: Event ID 16# 38C4 Distributed I/Os: station return Address of the affected DP slave: station number: 20 DP master system ID: 1 Log. base address of the DP slave: Input address: 8166 Log. base address of the DP master: 8190 Requested OB: Rack failure OB (OB86) Priority class: 26 External error, Outgoing event 07:34:49.459 AM 09/11/2018 Tehre are I/O access error, reading and writing events
AttachmentDiagnose.txt (169 Downloads) |
This contribution was helpful to
1 thankful Users |
9/11/2018 3:13 PM | |
Joined: 9/27/2006 Last visit: 9/24/2023 Posts: 12153 Rating:
|
Hello seko; If I had such a diagnostic buffer upload, I would be worried about my network installation. The OB122 calls refer to station addresses accessed in your CPU but not located through the network, so they coordinate with the OB86 calls (station failure).The number of failing stations would cause me to think that you have either a termination issue (losing power on one of the endstations, which causes reflections on the bus that can lead to station failures) or cabling issues (bad wiring, non-connected shield in the connectors...). Vibrations on the installed nodes can also cause intermittent loss of contact with the master. Look at the following basic documents, they should provide suggestions on what to look for on your network hardware: https://us.profinet.com/top-5-reasons-your-profibus-network-failed/ Then take a tean out and systematically examine every node on the bus for proper termination and adequate connections of the cable and connectors. Hope this helps, Daniel Chartier |
This contribution was helpful to
3 thankful Users |
Follow us on